Welcome to our new website! Learn more

Connection

  1. Connection to the district’s public sewer shall be made at a downstream angle of 45 degrees. The flow line of the lateral shall be above the spring line of the main and shall drop down to enter the main in accordance with the district’s standard detail, as instructed.
  2.  Connection shall be made using an approved wye fitting & couplings where lateral stub is not provided.
  3.  When connecting into a manhole, the connection shall be made at flow line of the main. If this is not possible, the connection shall intersect the manhole no more than a few inches above the bench.
Close window